Where do the 4 220vac wires go in the 3 prong receptacle? This is for a range...

XenoSapien
Sep 29, 2007, 05:00 PM
What are the colors of the wire? Black/white/red/green? This will help all those who answer.

XenoSapien

donf
Sep 29, 2007, 09:19 PM
The individual wires do not attach to the receptacle. They connect to the range. You need to change the receptacle to a four female faced receptacle.

Why are you changing out the line cord? Is the existing one damaged?

labman
Sep 30, 2007, 09:56 AM
The range should have terminals for 2 hots, the red and black, and one for white, the neutral. The ground connects to the metal cabinet. Older 3 wire installations connected the white to both the neutral and the metal cabinet. If you have 4 wire service, the safest thing is to upgrade to a 4 prong outlet and cord. It also removes any doubt about code compliance. Make sure the rating of the breaker, wire, receptacle, and cord match, and exceeds power the range takes.

Stratmando
Sep 30, 2007, 11:44 AM
If you have 4 wires, I would get 4 wire receptacle, and change out Range cord, so the Neutral and ground are separate, required for New and Remodel.