View Full Version : Why should I run 12/2 wire instead of 14/2 wire?


spdjnky
Feb 9, 2011, 04:25 PM

ballengerb1
Feb 9, 2011, 04:34 PM
You run 12/2 if you want to step up to 20 amps. 14/2 is only good for 15 amps.

Missouri Bound
Feb 9, 2011, 10:12 PM
If you really have to ask, you shouldn't be doing your own electrical work.

donf
Feb 10, 2011, 08:04 AM
Just to piggy back on Ballenger's response.

A 12/2 AWG cable would be used for circuits where the higher amperage is needed. For example, I have an commercial grade laser printer in my home office. This printer places a 18 or 19 amp demand on the circuit in short bursts. If I use a 15 amp circuit, the lights in the room will dim every four seconds because of the demand put on the circuit by the printer, so I installed an independent 20 amp circuit for the printer.

Probably a better description would be a high end entertainment center. If the overall demand will cause a 15 amp circuit to trip, you would install a complete 20 amp circuit.

Also, if you install a 12/2 AWG cable you can use either a 20 amp breaker or a 15 amp breaker. However the inverse is not true. If you install a 14/2 AWG cable you can only use it as a 15 amp circuit.

If you mix the two cables (part 12/2 and part 14/2) the entire circuit cannot be larger than a 15 amp circuit.

spdjnky
Feb 10, 2011, 05:36 PM
Thanks all and I guess my ? Wasn't worded right because I was just try to make sense out of the old wiring in my garage that I am taping into rather then run more new than I have to.I have a 20 amp circuit with 12/2 wire to a juntion box and from there goes to 2 outlets and a light that's it.I am going to run 2 outlets and 6 lights off that with 14/2 and change the breaker to a 15 amp.I was just trying to figure out why they wired my garage that way back in 1950.

Stratmando
Feb 10, 2011, 06:02 PM
I would keep the 20 Amp breaker, and the current Number 12 wire, and run # 12 for the rest. The difference in cost is minimal between the 2. it may get cold and you may want to plug in a heater. Don't Skimp. How much will you save?

donf
Feb 10, 2011, 06:26 PM
Hold on, in a garage you want the receptacles on a 20 amp circuit.

Under current code (2008) the receptacles are also required to be GFCI protected.

While you can install lights on a GFCI device it is not recommended to do that because if the receptacle trips and opens the circuit, there you stand/sit in the dark.