Ask Experts Questions for FREE Help !
Ask
    jimboace's Avatar
    jimboace Posts: 2, Reputation: 1
    New Member
     
    #1

    Oct 7, 2007, 02:54 PM
    Electric Power to Outbuilding
    My house has 200 amp service. I am running power to my new shed 250 feet from the house and need no more than 60 amps. What size wire (direct bury) do I need and should I be looking at copper or aluminum?

    Also, is there a formula to calculate the wire size based on amps, distance, voltage drop, etc. that a layman can use? Thanks.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #2

    Oct 7, 2007, 04:29 PM
    No calculations are necessary. The cable sizes are specified by the NEC Code.

    I've read that #6 is rated at 55 to 60 Amps (copper). I suspect that you would need to go to #4 for alum. However, I am not an expert on code and I am not a professional electrician.

    If it were me doing the work and cost was not an object I would opt to use the #6 UDS cable. UDS (Underground Distribution System) cable is direct bury. I'm not sure that UF (Underground Feeder) cable is direct bury,

    One more word of caution, if you go with direct bury cable, plan on trenching 26 inches deep and adding 2" of sand, then the cable, then the back-fill.
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #3

    Oct 7, 2007, 05:12 PM
    In fact for longer lengths you do need to do voltage drop calculations and perhaps use heavier wire. I try to leave questions like this to tkrussell and feel you can trust his answers.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Oct 7, 2007, 06:10 PM
    You will need to use #4/0 aluminum to keep the max recommended voltage drop at or below 2%.

    The cable charts in the NEC do not take long runs into consideration. Any over 100 foot and/or loaded 100% require voltage drop calcs be done.

    I use:

    2 x length of circuit x max amps x ohms per 1000 ft of chosen wire, see tables in NEC for resistance of various wires and power sources.

    Divide result by 1000 will arrive at the actual volts dropped.

    2 x 250 x 48 (80% of 60) x .33 Ohms for #4/0 Al,PVC conduit,AC / 1000= 7.9

    2% of 240 is 7.2.

    This is a excessive length for 120/240 volts.

    Copper would be excessive cost.

    You may want to consider using step up and down transformers to run at a higher voltage but allow for smaller wire.

    Transformers are costly also, close to $1000.00 for the two you need.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Heater - Seems to have no electric power [ 27 Answers ]

Hello everyone, I have a rather new (3-4 yrs) Goodman 92 heating system. It was not responding at the thermostat so I tried resetting stuff there, etc. with no result. In checking the heating unit, I see that my Honeywell Enviracare has no power light lit and the heating unit seems to be in...

$500! Electric bills// power -save 1200 any info? [ 1 Answers ]

I have been seaching for ways to save on electric bill over $500 a month last three months And looks to be that way a couple more. I ran across this Power-Save1200 web-site. Does anyone know if this works? Any other suggestions would be a great help.! going broke!

Power pole that electric company won't fix. [ 3 Answers ]

So I'm helping my friend with this problem. He lives on a lot with a private power pole. Recently it shifted and the meter (which is on the pole) disconnected from the breaker that feeds into his house. So now he is without power, I've contacted a contractor to set the pole straight, but he said...

Kenmore electric dryer/ no power [ 1 Answers ]

I have an electric kenmore dryer, seems like it is not getting power. I have checked the breaker everything is fine there took off the back panel and have tested that it is getting power as far down the hot wire as I can check that leads to the blower motor. Even when you open the door there is no...


View more questions Search