    I have a 30KW 3 phase generator I purchased from government surplus. After repairing the generator it runs fine and I will only be using 2 of the phases. Now my question. I have a new Cutler-Hamer model DT224URK-NPS 200 amp transfer switch which I have mounted above where my service enters my home. The switch is after my meter and main cut off breaker. The service to my home is 4/0 aluminum with 2/0 neutral and 4AWG ground. I can disconnect and pull the wire back from my main breaker box and feed the transfer switch with not much problem. The feed is long enough. What I want to know is can I use 2/0 copper feed, 2/0 neutral and 4AWG ground from the switch back into my breaker box or do I have to use the 4/0 aluminum feed wire? This would make the job much more easy.

    Thanks much

    Forrest
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Oct 2, 2007, 02:27 AM
    The load side can be copper wire.

    What you need to watch out for is any 240 volt loads in your home. They will not run to full operational power due to the 208 volt that will be delivered by the generator. Esp motors, which probably you don't have many, maybe a well pump.

    Also, need to be careful of the generator, It will not like being loaded only on two phases.

    Keep in mind, that a main breaker must be first in line before feeding the transfer switch, otherwise there will be no short circuit protection for the switch.
    fdilley's Avatar
    fdilley Posts: 3, Reputation: 1
    New Member
     
    #3

    Oct 2, 2007, 01:49 PM
    Thanks tkrussell. The other phase is to be used by my neighbors. All the loads in the house are resistive (hot water tank, range etc.) I don't think I should have a problem with a loss of 32 volts. And the meter and disconnect breaker is before the switch. One other question, should I bond the ground and neutral at the generator or just ground the generator? I have an 8ft ground rod at the generator.

    Thanks again.

    Forrest
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Oct 2, 2007, 02:32 PM
    Oh I now I have heard everything, the neighbor will use the third phase! I don't even want to know how he will wire that. La La La I hear nothing...

    Do not connect the neutral to the equipment ground at the genset. The transfer switch will not break the neutral, so you will have a non-separately derived system.


    You may notice a loss of heating time with the electric elements in the appliances. No harm will be done to anything other than slower heating.
    You may drive the rod to ground the frame and equipment ground, but not necessary.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

3-way switch as transfer switch? [ 47 Answers ]

Why are transfer switches so expensive? What's wrong with Using a 3-way switch for each circuit that I want to connect To my generator?

Installing transfer switch at gas furnace [ 2 Answers ]

I purchased the Reliance TF201W Easy / Tran switch. I'm planning to install it so I can run my gas furnace off my generator via extension cord this winter if necessary. The installation instructions show the switch being wired into the breaker panel. My breaker panel is in a finished basement...

Transfer Switch [ 3 Answers ]

Ok I am looking to add a transfer switch so I can run my generator when the power is out. I have always been told that my transfer switch needs to be rated higher then my generator's output. The problem is my generator has two output rating stated. In other words, a constance rating of 5,550 kw...

Schmatic of a transfer switch? [ 2 Answers ]

I'm trying to find a schmatic of a 6 braker 20 amp manual transfer switch for mr 5000 what generator... I d like to see how they hook up and know just how they work... will I have to turn off my 200 amp main or will the manual transfer switch do it? Or maybe it don't get turned off?I did see...

Transfer switch [ 6 Answers ]

I’ve recently purchased a Guardian 13kw standby generator with a transfer switch and load center panel. I have a couple of questions 1. The transfer panel had a total of 205 amps through 12 various breakers in it, can I replace some of them as long as I don’t go over the original 205 amps and use...


View more questions Search