    3-prong generator & 4-prong power cord
    My 5kw Coleman Powermate generator has two 110v receptacles and two 220v receptacles. Both of the 220v receptacles are the 3-prong blade type. My six circuit Reliance ProTran transfer switch has the 4 prong female twist lock. Both ends of my 30amp 4-wire cord are twist lock. The end for the transfer switch is no problem. My Coleman manual states if I am going to use the 220v receptacle to power up any 110 circuits, I have to use the transfer switch. It also says I have to have an adapter plug inserted into one of the 110v receptacles. Something I didn't understand about floating and bonded grounds. It says the ground and neutral terminal on the adapter plug has to have a jumper wire connecting the two together.
    I was going to buy a three blade male plug that fits the configuration of the 220v receptacle on the generator. I thought I could cut off the male end of the 30amp power cord and hook the wires up to the new plug. My plan was to just connect the white neutral wire and the ground together on the new plug. Will this be the same thing as making an adapter plug and pluging into one of the 110v circuits? Will it work? Any other alternatives? Thanks, Steve
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #2

    Sep 17, 2008, 07:02 AM
    I'm only slightly confused.

    GIVENS
    With the 240 receptacles you have 2 hots and a ground.
    In order to get the neutral, you have to get it from the 120 V outlets.

    Let's assume that all the grounds of the receptacles are tied together and assume that the transfer switch does not switch the neutral.

    EDUCATION
    A system requires that ground an neutral be tied together at one place. In the home there is one place where the neutral and ground and a ground rod come together.

    Generally when a generator is used to power a house the neutral/ground bond is removed and that takes place in the house.

    CONFUSION

    As I see it. If the transfer switch is used alone then the ground and neutral need to be bonded together at the generator.

    If the transfer switch is used in combination with a household panel where there already should be a bond between ground and neutral, you need to get the neutral and ground from the 120 V receptacle and get the two hots from the 240 V receptacle.

    So, in this case the ground will be bonded to the neutral in the same place that the house bond occurs.

    It is important that this bond occurs, but occurs only once.
    vegasSteve's Avatar
    vegasSteve Posts: 3, Reputation: 1
    New Member
     
    #3

    Sep 17, 2008, 11:08 AM
    Thanks, I intend to use the transfer switch wired into the main panel to power up 6 circuits in the event of a power failure. What I need to know, given the configuration as stated, is what do I need to do to the one end of the power cord to get it to work with the 240v blade type receptacle on the generator. The cord is a male twistlock 4-wire, that I thought I could cut off and wire into a new 3-prong male blade type plug. Do I still need to make up an adapter plug to stick in one of the 110v receptacles or not, if I incorporate the white and green wires together on the new plug
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #4

    Sep 17, 2008, 01:14 PM
    This explains things a little more than I can:

    Portable generator neutral rewiring

    I just checks on the Coleman site and nothinng there can help me.

    I'd suggest to do the neutral ground check as outlined above. No neutral ground bond.

    If it fails, then your in good shape providing the transfer switch does not switch the neutral. High probabbility.

    You will then need to make a "Y" cord that grabs the two hots from the 240 recptacle and the ground. You will then connect the neutral wire to the 120 V recepacle.

    In your best interest, I think it's best interst to mount a 4 wire twist lock on the generator.

    Then for portable operation wire a twist lock plug with ground and neutral jumpered together, so you comply with code.

    That takes care of it.
    rschlack's Avatar
    rschlack Posts: 5, Reputation: 1
    New Member
     
    #5

    Jan 1, 2013, 03:45 PM
    I have a very similar question but my generator is 3500 watts with a 3 prong 120v 30amp female. My house has a 4 prong twist lock going into a 30 amp circuit breaker.

    Can I just take the end of my 4 prong cord off, tie the neutral and ground together and put on a 3 prong male end?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #6

    Jan 1, 2013, 04:19 PM
    That is not what makes it a 3-prong.
    The generator is 120V, the house inlet is 120/240V.
    You can make a cheater cord but it will only provide 120V to the house so you will have to shut off any 240V breakers.
    rschlack's Avatar
    rschlack Posts: 5, Reputation: 1
    New Member
     
    #7

    Jan 1, 2013, 04:30 PM
    Yes, I will only use it to power a few 120v items. But I just don't want to o anything that would cause bad things to happen. Am I correct in thinking that I can tie the neutral and ground together to get just a few essential items up and running?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #8

    Jan 1, 2013, 04:32 PM
    But why do you think you need to do this?? The N & G are separate in both the generator and the house inlet.
    rschlack's Avatar
    rschlack Posts: 5, Reputation: 1
    New Member
     
    #9

    Jan 1, 2013, 04:38 PM
    The cord has 4 wires, 2 hot, N and G. The generator has 3 prongs. So I just thought that 1 of the 4 wires has to go.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #10

    Jan 1, 2013, 04:41 PM
    Right. Your generator has ONE hot, neutral and ground.
    You need to jump out the two hots at the house end of the cord.
    rschlack's Avatar
    rschlack Posts: 5, Reputation: 1
    New Member
     
    #11

    Jan 1, 2013, 04:47 PM
    Thanks for the advice.

    Rob
    rschlack's Avatar
    rschlack Posts: 5, Reputation: 1
    New Member
     
    #12

    Jan 1, 2013, 04:48 PM
    Thanks for the help

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Replacing 2-prong receptacle with 3-Prong -NO GROUND WIRE [ 6 Answers ]

Hi there! I was wondering if someone can tell me how exactly I go about doing this safely. I have an existing 2 prong ungrounded plug... theres no ground to this receptacle... old metal box does not seem to be grounded either. I would like to replace this receptacle with a 3 prong GFCI...

How do I adapt a 3 prong cord to a 2 prong? [ 2 Answers ]

What can I use to reduce a new 3 prong extension cord to the 2 prong cord on Christmas lights? I know they must make something for this problem!:confused:

3 prong to 4 prong dryer cord [ 3 Answers ]

Hello, I wanted to know when converting to a 4 prong dryer cord , what do you do with the green ground wire that is already connected to the frame. Do I replace it with the green ground wire that's on the cord or do I leave it alone, and place the green wire from the cord on another screw.

Changing 4 prong dryer plug to work with 3 prong outlet [ 1 Answers ]

I have a dryer I haven't been able to use. I moved into an older house and bought a wall outlet to match the plug that's on the dryer. The problem is, any way I rewire the outlet with given wires it won't work.

What is the difference in a 2 prong or a 3 prong condenser motor capacitor? [ 1 Answers ]

Hello, 1996 Rheem AC (SEER 12) condenser fan moter replaced. (A.O. Smith 1/8 HP 825 rpm. 208-230 volt.) My old capacitor has 3 prongs, black, black and white. The white one has an orange wire that goes to the compressor. The new capacitor has 2 prongs, black and black. Where do I...


View more questions Search