    Furnace blower won't turn on?
    Carrier furnce, when i set thermostat to fan on, blower won't come on, but when i run the heat the fan will come on like it is suppose to,anyone have any suggestions. Thanks
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #2

    Aug 3, 2011, 07:54 PM

    Several possibilities like a failed switch on the stat or more likely a bad control board in the furnace. Does your control panel inside the furnace have any small red or orange lights blinking? This would be a failure code. Open the panel or look for a small peep hole to see the lights
    VL's Avatar
    VL Posts: 6, Reputation: 1
    New Member
     
    #3

    Aug 3, 2011, 08:22 PM
    No lights, i did put in a new honeywell thermostat, maybe i have it wired wrong.
    drtom4444's Avatar
    drtom4444 Posts: 3,282, Reputation: 145
    Ultra Member
     
    #4

    Aug 4, 2011, 08:17 PM
    Your fan relay is bad. It is cheap to fix, but make sure your coils and the fan blower wheel are clean, too. You can get a new fan relay for $5-10. Make sure you wire it correctly or you will burn up the fan motor. DrTom4444
    VL's Avatar
    VL Posts: 6, Reputation: 1
    New Member
     
    #5

    Aug 5, 2011, 04:31 AM
    Thank you, dr. tom4444, also, my ac won't turn on, any suggestions where to start. Thanks.
    VL's Avatar
    VL Posts: 6, Reputation: 1
    New Member
     
    #6

    Aug 6, 2011, 08:26 AM
    If i jump r -power to g - fan on circuit board the fan blower works, the fan runs continually, once i remove the jumper connection it shuts off, but if i move the green fan control wire to gh, another spot that's empty on the circuit board the fan works, would it be okay to leave it there or will this cause other problems? Thank you.
    drtom4444's Avatar
    drtom4444 Posts: 3,282, Reputation: 145
    Ultra Member
     
    #7

    Aug 6, 2011, 09:34 PM
    If you can jump it like that it is a problem in the t-stat. It won't hurt anything to leave this on. If the AC will not work either then there is a problem in the t-stat, most likely. You need to turn on the AC and see if you have a voltage reading of 24-30 volts between R and Y. If so, then the problem is in the t-stat. If there is no voltage and you have 24 volts at Common and Y then the problem is in the contactor or a safety switch is tripped or there may be no power at the outside unit. You just have to let the meter be your eyes. DrTom4444
    VL's Avatar
    VL Posts: 6, Reputation: 1
    New Member
     
    #8

    Aug 9, 2011, 08:47 AM
    Thank you drtom4444, with the power on to the ac nothing happens, it doesn't turn on, but when i hold down the contactor it runs and cold air comes out of the ducts, does that mean the contactor is bad or a problem with the thermostat or could it be something else? Also, while i'm at it i figure i should change the capacitors and fan relay, the motor run capacitor is not looking to good and they don't seem to be that expensive, what is your opinion on that. Also i am going to clean the evaporator coil, but i have the old uncased type made of a sheet metal box housing, i have access on three sides, any idea what is the best place to cut out an opening, i know the newer ones give you access in the front, so any feed back would be helpful, thanks again and looking forward to your commentary.
    drtom4444's Avatar
    drtom4444 Posts: 3,282, Reputation: 145
    Ultra Member
     
    #9

    Aug 10, 2011, 12:06 PM
    One rule is that you do nothing unless the meter says you need to do it, with a few exceptions. Is the contactor getting 24 volts? If so and it will not pull in then you have a bad coil and you need a new contactor. On the coil you should cut out the side where the pipes go in and slide out the coil. To do it right you should pump down the unit which means to close the high side valve at outside unit and run unit to pump gas into condensing unit. Most gas should be put into a recovery can first. Then when pressure is zero cut lines and take out coils and seal them up well. You need ox-acetylene torches to do this. You then use alkaline coil cleaner (liquid lye) to clean coils along with a 1500 psi pressure washer. Hope this helps. DrTom4444
    cynistersix's Avatar
    cynistersix Posts: 1, Reputation: 1
    New Member
     
    #10

    Jul 6, 2014, 05:10 PM
    I had a similar issue. For my unit the only thing not connected at all was the G to G connection from the Unit to the Thermostat
    drtom4444's Avatar
    drtom4444 Posts: 3,282, Reputation: 145
    Ultra Member
     
    #11

    Jul 6, 2014, 07:49 PM
    The "G" wire from the thermostat to the unit is the fan relay wire. On the coil for the fan relay you have common and "G." "R" and Common leave the 24 volt transformer secondary. "R" supplies the side of power that is switched in the thermostat. Common goes to the one side of the fan relay, the condensing unit contactor, and the reversing valve that is not switched by the thermostat; however, sometimes common is run through safeties so that when a safety trips it will drop out everything.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Furnace blower won't turn on? [ 1 Answers ]

I just finished installing Honeywell RTH2410B thermostat and AC does not turn on either on auto on fan on. I have already tried turning breakers on and off. Need help any ideas?

Furnace blower won't turn on [ 3 Answers ]

I have a Coleman Presidential 2 furnace in a mobile home. The pilot is lit and the thermostat clicks the furnace on, but the blower will not engage. After a few minutes, the furnace shuts down (to pilot light only). I had the same problem last year, but a cleaning solved the problem. Any advice...

Blower in furnace does not turn on [ 6 Answers ]

Gentlemen... turned air on for the 1st time this year. a/c unit outside fires up fine... but blower in furnace does not. Replaced thermostat during winter because blower would not shut off. After installation furnace worked as it should. I must have wired thermostat wrong? Thanks for any and all...

Blower for furnace won't turn on [ 2 Answers ]

I have just re-lit my pilot light for the winter. The furnace is turning on with the thermostat set, but the blower isn't. If I put the blower to manual it turns on, but not in the auto setting. What do I need to do?

Furnace blower won't turn on [ 8 Answers ]

I have a Bryant 395C furnace. The blower won't come on even when thermostat fan switch is set to "on." I've verified that I'm getting 24V AC between terminals marked G and C on the furnace. Blower has 3 wires going into circuit board on furnace. These are colored red, black, and white; red is...