    Can I run 400 amps with two 200 amp boxes?
    I want to run 400 amp service in my new home and I was wondering if it is possible to run two separate 200 amp boxes instead of 1 400 amp with is much more expensive. If so do I need a main 400 amp lug or can I use the two separate 200 amp mains?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Dec 30, 2006, 04:32 PM
    Sure, you will need a 320 amp meter socket with two 200 amp breakers to feed the 2 200 amp panels.

    See this previous post for a picture:
    https://www.askmehelpdesk.com/electr...ighlight=meter
    jimmyj71's Avatar
    jimmyj71 Posts: 6, Reputation: 1
    New Member
     
    #3

    Jan 1, 2007, 06:29 PM
    TK... thanks for the reply. Do you know where I can get a detailed wiring diagram either online or in book form? Most home electrical books do not get into this type of wiring. Thanks

    Jim
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Jan 1, 2007, 07:55 PM
    What type of wiring? For feeders?
    jimmyj71's Avatar
    jimmyj71 Posts: 6, Reputation: 1
    New Member
     
    #5

    Jan 4, 2007, 07:28 PM
    I need to see how the meter socket is wired to the two panels. I have wired several panels and have done much remodeling over the years but I have never run two boxes like this and I have had no experience with wiring a meter socket. If I can just see how it is wired I should have no problem. Thanks!

    Jim
    dei2007's Avatar
    dei2007 Posts: 12, Reputation: 1
    New Member
     
    #6

    Jan 4, 2007, 07:58 PM
    Quote Originally Posted by jimmyj71
    I want to run 400 amp service in my new home and I was wondering if it is possible to run two separate 200 amp boxes instead of 1 400 amp with is much more expensive. If so do I need a main 400 amp lug or can I use the two separate 200 amp mains?
    You will have to use (2) 200 panels inside the house and use a double lug meter base outside.The reason that's is because your power company will only hit the meter base 1 time.What you will have to do is run 4 ought aluminum (4 wire) from each 200 amp panel inside the house.Just tell them at your supply house that you need a 400 amp meter base.Let me know if this helps.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #7

    Jan 4, 2007, 10:09 PM
    See page 38 of the Milbank catalog for a typical 320 amp meter that has two 200 amp breakers, each to feed a 200 amp panel.

    Hard to find a wiring diagram as this is very basic, two hots from each breaker to a panel, along with the neutral and equipment ground. All you need to do is know how to wire one panel, times two.

    The previous answer, suggesting a 400 amp meter is incorrect. These meters will all be rated 320 amp.

    You can use #4/0 SER Aluminum cable, which will have two 4/0 for the hots, one 4/0 for the neutral, and one #2/0, see page 3 of the Alcan catalog, and read the manufacturers instructions.

    If you use PVC conduit you can use 2" with 3 # 2/0 Copper and 1 #4 copper for the equipment ground.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

2 200 amp disconnects and a 200 amp meter [ 3 Answers ]

On a new house I have 2 200 amp panels on the inside. What will be the best way to hookup the 2 200 amp outside disconnects and meter to look decent for the house?:o

200 Amp [ 1 Answers ]

I Am Having A Home Built That Is 3800 Square Feet. The Home Will Have 2 Furnaces, 2 Air Conditioners, 2 Refrigirators, And A Deep Freeze. All Other Appliances Will Be Gas. I Have Voiced Concerns About The Availability Of Unused Circuits On The 200 Amp Panel To Be Able To Finish The Basement In...

200 amp or 100 amp [ 6 Answers ]

Which is better, a 100 amp circuit box or a 200 amp circuit box?

200 amp service with a 200 amp outdoor breaker [ 1 Answers ]

I need to know how to wire a 200 amp outdoor breaker enclosure.I have 4/0 scu cable for my service head to the meter,and 4/0 scu from meter to breaker enclosure.Then from the breaker enclosure I have 4/0 ser cable to my panel.What is the proper wiring method in the enclosure,please help.

200 amp [ 2 Answers ]

Looking for opinons for panel boxes ge square d cutler hammer murray Also what does 30/40 spaces mean. Thanks for any info.


View more questions Search