Ask Experts Questions for FREE Help !
Ask
    mhudalla's Avatar
    mhudalla Posts: 7, Reputation: 1
    New Member
     
    #1

    Feb 9, 2010, 07:13 PM
    Carrier Weathermaker problems squared
    Hello- I have two Carrier WeatherMakers (58SX)

    Furnace number one: Inducer motor won't start

    Furnace number two:
    Just started acting up today. Last year we had a service company replace just about everything in this unit with poor results and a heck of a lot of $$$$. As a last resort I ran new thermostat wire and it has been fine up until today. The furnace works but I had to flip the SSR switch twice to get it to restart when the thermostat re calls for-heat.
    letmetellu's Avatar
    letmetellu Posts: 3,151, Reputation: 317
    Ultra Member
     
    #2

    Feb 9, 2010, 08:07 PM

    Furnace number !:
    If nothing happens when you turn on the thermostat it could be many different things.
    First make sure you have power to the unit.
    Next make sure that the door switch is making a connection when it it closed.
    Next make sure the fuse on the board is not blown, if so replace it with a 3 or 5 amp fuse.
    Next when thermostat is calling for heat make sure you have power to the inducer motor. About the only way to do this is with a volt meter ( A real meter and not one that just makes a light glow).
    If you don't have power at the motor and after you have determined that you have power to the furnace board by checking the voltage at terminal L1and L2. If you have powere use the meter to check Primary L1 and primary L2. If you have power then connect the R terminal to the W terminal on the circuit board with a jumper wire. If you get something to start that means something is wrong with the thermostat or the wires going to it.

    Furnace 2: I am not sure what the SSR switch is, so tell me what it is and also is the unit still working right now. If not you can use some of the test above to find the problem.
    mhudalla's Avatar
    mhudalla Posts: 7, Reputation: 1
    New Member
     
    #3

    Feb 9, 2010, 08:29 PM
    Thank you for your response. Everything checks out on your list up to the fuse. I will check voltage the voltage. Is there a chance it could be the ignitor?

    Furnace 2: I was referring to the switch, (looks like a wall switch) outside of the unit

    Thnak you again for your time!
    letmetellu's Avatar
    letmetellu Posts: 3,151, Reputation: 317
    Ultra Member
     
    #4

    Feb 9, 2010, 08:39 PM

    If the inducer motor will not run it is not the ignitor, the ignitor will not try to glow until the inducer has run for about 30 seconds.
    letmetellu's Avatar
    letmetellu Posts: 3,151, Reputation: 317
    Ultra Member
     
    #5

    Feb 9, 2010, 08:46 PM

    On furnace one what happened when you jumpered the R terminal and the W terminal on the low voltage section of the board.
    mhudalla's Avatar
    mhudalla Posts: 7, Reputation: 1
    New Member
     
    #6

    Feb 13, 2010, 08:45 PM
    Hello-
    Furnace number one.:
    I have power to the board. I jumped between R and W with no results. I would like to put a meter on the Inducer, but it's power connector slides directly onto a small transistor board. Also something to note, when I turn the power on the black box on the top right that with the orange wire that goes to the ignitor clicks. Also, if I turn the power on and off sevral times, the furnace blower can be tricked into running.

    Furnace number two had a poor connection and is running fine now.
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #7

    Feb 13, 2010, 10:11 PM
    If the inducer won't run, the "transistor board" (actually referred to as the inducer control board) may be the problem. Try this: dismount the pressure switch from the inducer control housing, set the thermostat for heat operation, and tap the relay on the inducer control housing with the butt of a screwdriver. If the inducer starts/runs, the relay contacts are burned/oxidized. Replacement of the inducer control will correct this problem. If kit #313680-751 is used, be sure to follow ALL the instructions included for adding the additional circuit to the control. Simply popping the board in will not solve the problem.
    Attached Images
      
    mhudalla's Avatar
    mhudalla Posts: 7, Reputation: 1
    New Member
     
    #8

    Feb 13, 2010, 11:00 PM
    Thank you for the great pictures. I gave the relay some good taps- no luck, could the pressure switch be the culprit?
    mhudalla's Avatar
    mhudalla Posts: 7, Reputation: 1
    New Member
     
    #9

    Feb 14, 2010, 08:33 AM
    Will I be risking any damage to the control unit of unit two if I use it on Furnace one?
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #10

    Feb 14, 2010, 08:54 AM
    It's not likely you would risk any damage, but it may not be productive. If you look closely at the inducer control board, you may notice that the cover can be removed from the relay. A pocket screwdriver will usually accomplish this. If the inside of the cover shows evidence of burning, the relay may be the problem. Try operating using the power supply switch, & with the thermostat set to demand heat. If the relay is engaging but the inducer does not run, CAREFULLY nudge the relay bridge with a screwdriver. If arcing at the contacts and/or motor operation is observed, you've identified the culprit. In a pinch, the contacts can be cleaned with a sliver of sandpaper, until the control can be replaced.
    Attached Images
      
    mhudalla's Avatar
    mhudalla Posts: 7, Reputation: 1
    New Member
     
    #11

    Feb 14, 2010, 09:08 AM
    Will do. And once again- thank you for your time- I really appreciate all the info!
    mhudalla's Avatar
    mhudalla Posts: 7, Reputation: 1
    New Member
     
    #12

    Feb 14, 2010, 10:55 AM
    I could not get the cover off the relay without amaging the board. So I switched controller units. Still no preheat/inducer action.
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #13

    Feb 14, 2010, 11:50 AM

    Did you try installing the inducer control from the non-functional unit on the functional unit? If you have a voltmeter, you can check for voltage output by removing the inducer control from the housing, and re-connecting the plugs to the control board. Touch the meter probes to the contacts where the inducer motor plugs in. If you measure approximately 115-125 volts but the motor doesn't run, the motor has failed. If no voltage is present, the problem may be in the pilot switch or fusible link.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Carrier Weathermaker 8000 [ 4 Answers ]

Hi, I am having a problem with my Carrier Weathermaker 8000, Last night when we went to bed, everything was fine, this morning when we woke up it was a chilly 61 degrees in our home. Our neighbor came over to try and fix the problem, but, now we can't get the heater to come on at all, before while...

Carrier weathermaker 8000 problems [ 0 Answers ]

We have a Weathermaker 8000TS... Generally the LED code is 34 or 14. The gas valve and the sensor have been replaced recently and the entire furnace and filters cleaned. All vents open an unrestricted. The furnace will glow then attempt to light (blue flame)... sometimes it catches, sometimes it...

Carrier weathermaker furnace [ 2 Answers ]

The inducer runs all the time even when on a/c. I need some help!

Carrier weathermaker furnace [ 1 Answers ]

The inducer runs all the time even when on a/c. I need some help!

Carrier Weathermaker not heating [ 1 Answers ]

We have a Carrier Weathermaker furnace approx 20 years old. The blower will work if we go and hit the switch off and on but no heat is coming out of vents. No problem till now. Checked filter and it does need replaced but there was still no heat when filter was removed. Not sure what to check....


View more questions Search