|
|
|
|
New Member
|
|
Aug 14, 2009, 05:52 PM
|
|
Calculate using 277v
How do you calculate wattage for 277v's?
Is it the same as 277(15A)=4155 watts (If the amps is 15)
If so, does this mean if I wanted to supply 150w (output) HID light fixtures that are 277v, I could supply 28 lights using a 15 amp circuit?
Just learning, not thinking of doing 3phase, but curious.
Also, where does 277 come from?
What with all the voltages (120, 240, 208, 240, 277, 480... I even seen 380?? )
Sorry for all the questions. My main question is the first one.
|
|
|
Ultra Member
|
|
Aug 14, 2009, 07:54 PM
|
|
Ohms law is consistent, everything else is variable. Your calculations will be accurate if you follow the rules.
|
|
|
New Member
|
|
Aug 14, 2009, 08:00 PM
|
|
Originally Posted by Missouri Bound
Ohms law is consistent, everything else is variable. Your calculations will be accurate if you follow the rules.
Really! That's interesting. Looks like you get more out of three phase than single. May be best to have everything 3 phase!
Another question: How do you get 277 from a 3 phase transformer. I still don't get it. I know 120(1.732)=207.84 or 208V. But where does 277 come from (line to neutral)?
|
|
|
Uber Member
|
|
Aug 14, 2009, 08:04 PM
|
|
277 = 480/sqrt(3) -----> Was 460. 480 is correct
|
|
|
Ultra Member
|
|
Aug 14, 2009, 08:07 PM
|
|
One thing to keep in mind with high intensity ballasted lamps... the ballasts consume energy as well, in addition to the lamp wattage. All ballasts (or fixtures) have amperage information on them. A 150 watt fixture may very well consume 200 watts. You need to check the fixture for this information when doing your calculations.
|
|
|
New Member
|
|
Aug 14, 2009, 08:09 PM
|
|
Originally Posted by KeepItSimpleStupid
277 = 460/sqrt(3)
That comes to 265.58
I just tried 480/1.732, and it came to 277.
Still doesn't make sense On why 277? Lost!
|
|
|
New Member
|
|
Aug 14, 2009, 08:12 PM
|
|
Originally Posted by Missouri Bound
One thing to keep in mind with high intensity ballasted lamps....the ballasts consume energy as well, in addition to the lamp wattage. All ballasts (or fixtures) have amperage information on them. A 150 watt fixture may very well consume 200 watts. You need to check the fixture for this information when doing your calculations.
I see! I was told (Dad--is an electrician. He has me researching, so I can have a better understanding of my venture) you could use input to calculate HID's?
|
|
|
New Member
|
|
Aug 14, 2009, 08:14 PM
|
|
Sorry, I mean output.
|
|
|
Uber Member
|
|
Aug 15, 2009, 01:03 AM
|
|
|
|
|
Uber Member
|
|
Aug 15, 2009, 10:00 AM
|
|
Basically there are two electrical ways to utilize 3 phase power. One being Wye (Y) and Delta. In the Y mode, the phase to phase voltage is 208 volts and phase to neutral is 120V or 208/sqrt(3).
The neutral is the center point or 0 volts in the system.
Similarly the 480/277 comes from the similar case where 480 gets replaced by 208 V and 277 gets replaced by 120V.
277 and 120 V are a phase to neutral voltages. Whereas 480 and 208 are phase to phase voltages.
|
|
|
New Member
|
|
Aug 15, 2009, 01:48 PM
|
|
Originally Posted by KeepItSimpleStupid
Basically there are two electrical ways to utilize 3 phase power. One being Wye (Y) and Delta. In the Y mode, the phase to phase voltage is 208 volts and phase to neutral is 120V or 208/sqrt(3).
The neutral is the center point or 0 volts in the system.
Similarly the 480/277 comes from the similar case where 480 gets replaced by 208 V and 277 gets replaced by 120V.
277 and 120 V are a phase to neutral voltages. Whereas 480 and 208 are phase to phase voltages.
Why not just use 277--if we can get more wattage, or voltage amps? I guess install three phase on residential houses id ridiculous!
|
|
|
New Member
|
|
Aug 15, 2009, 01:51 PM
|
|
Originally Posted by KeepItSimpleStupid
Thanks for the links!
|
|
|
Uber Member
|
|
Aug 15, 2009, 04:14 PM
|
|
It's rare to have 3 phase for residential, but it does happen. Three phase motors are more efficient and that's usually what happens in commercial. Cooling and heating take motors.
Lighting in commercial spaces is 277 V usually.
Our bi-phase 240 is probably a little safer than other 240 system.
Some countries, like Japan have a 100V system. Usually the frequency is 50 or 60 hz.
|
|
|
New Member
|
|
Aug 15, 2009, 05:29 PM
|
|
Originally Posted by KeepItSimpleStupid
It's rare to have 3 phase for residential, but it does happen. Three phase motors are more efficient and that's usually what happens in commercial. Cooling and heating take motors.
Lighting in commercial spaces is 277 V usually.
Our bi-phase 240 is probably a little safer than other 240 system.
Some countries, like Japan have a 100V system. Usually the frequency is 50 or 60 hz.
I see, thanks!!
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
277V lighting switch installation
[ 1 Answers ]
I want to replace a three-way switching configuration for a 277v circuit with a single-switch configuration. The current configuration has gray and brown wires in addition to the orange wires, which I assume are the travelers. How do I wire up the one-way switches?
277v HO light on a 2 Phase System... Can it be done?
[ 7 Answers ]
I tried to find tkrussell's previous post when he explained 1 phase, 2 phase and 3 phase - as it relates to voltage. The lights I want to install are Cooper's XF Falcon floodlights 250w MH - they say they are 277v and are "tritap 120/277/347"
I remember something about 277v not being 240v? Is the...
277v wiring
[ 2 Answers ]
When wiring lighting or other devices on a 277v system, what colors go to what phase, in what order? I know the colors, but was asked on a test for employment this question, and I can't figure it out on a 3 phase system.
View more questions
Search
|